Ok, so the inverter bypass circuit is getting power via circuit breaker 5. There is a 16A (or a 12A depending on which document you read) breaker on the inverter that has to be reset if you have a fault or overload that circuit. 16A is a kinda weird cb rating. What is the current rating of cb 5, they should have the same current running through them?
When there is no shore power and you are running in inverter mode, the output is limited to about 1000w/8A continuous. There is apparently no cb for this mode, it is internally monitored by the inverter and is reset by cycling the power button off and back on.
Over to the 12Vdc side. The unit is supposed to be supplied with minimum 4 awg wire protected by a 100A inline fuse. Did FR install that correctly? Hopefully the fuse is at the battery where it should be???
BTW, the 100A looks to be the correct number based on the 1kw continuous rating and the 86% efficiency, but 4 awg is too small for 100A, it should be 2 awg. Also, I would bring a spare 100A fuse along, fuses and cb's should be sized 25% larger than the continuous load they might see to prevent nuisance tripping.