offgrid ![]() Senior Member ![]() Joined: 23 Jul 2018 Online Status: Offline Posts: 5290 |
![]() Posted: 20 Feb 2021 at 6:20am |
Toyanvil, I only pointed out sections of the Code that explicitly deal with what are obviously dc circuits to show that they are covered. I was not suggesting they were the only sections covering dc circuits. The way the NEC works is that it’s prescritive, meaning that unless there is an exception noted you have to do what it says. There are no such general exceptions for say 12V dc circuits so you have to follow all the applicable Code articles for those systems just like you would for 120Vac. So that means if you are wiring up an off grid home at 12 or 24Vdc you need to maintain a contiguous grounded neutral and place all your disconnects and over current protection in the hot line, just like in a grid powered building.
That is for an off grid residence. If that residence is subject to electrical inspection then it would be reviewed for code compliance just as if it was ac powered. I have seen many such systems installed by my solar customers rejected for not following the NEC. As for what an electrical inspector would say about an RV, most likely he’d just say he doesn’t have jurisdiction over it and wouldn’t look at it. That leads us back to NFPA 1192 and the RVIA low voltage standard which I am too stingy to drop $45 on. That and the NEC are going to be the most appropriate US standards for electrical systems in RV’s. If anyone wants to “crowd fund” me to get the standard and review it I’ll be happy to 😄. Your current 4 way switch in the positive battery leg is a good example of why the battery disconnect should be in the positive line. By keeping everything that can open the circuit in the ungrounded (positive) line you always keep a solid ground reference (negative) and can manage multiple sources without inadvertently connecting things together that shouldn’t be or disconnecting things that should stay connected. When you get into more complex circuits with multiple sources like solar, generators, grid supplied chargers, inverters, multiple battery banks, etc etc you can easily find where they hid the smoke unless you keep a common ground reference. |
|
1994 Chinook Concourse
1995 RV6A Experimental Aircraft 2015 Rpod 179 - sold |
|
![]() |
|
Toyanvil ![]() Senior Member ![]() Joined: 15 Feb 2019 Location: Bakersfield Online Status: Offline Posts: 157 |
![]() |
Both ways work the same and are good, it sounded like it would work better for the OP to switch the ground side of the battery without a lot of work and that's how I would do his. The funny thing is, I have dual 12 volt batteries and my switch is on the positive side. Only because my switch has 1-2-both or off setting so I have no need to install a disconnect only switch.
|
|
![]() |
|
pedwards2932 ![]() Senior Member ![]() Joined: 21 Sep 2020 Online Status: Offline Posts: 333 |
![]() |
I was just going by how all the boats i delt with were wired as all the larger ones have battery switches and they are always wired from the positive terminal......I just figured a TT would be similar.
|
|
![]() |
|
Toyanvil ![]() Senior Member ![]() Joined: 15 Feb 2019 Location: Bakersfield Online Status: Offline Posts: 157 |
![]() |
offgrid, I was only trying to show there are two ways of installing a switch. I am a building engineer and am familiar NEC code book and have not seen a code that would apply here. Article 480 covers storage batteries, like the ones in my UPS systems and Article 690 provides the circuit requirements for PV systems (solar photovoltaic) I too would like to know what code an inspector would refer to for a 12 volt DC switch on an RV.
|
|
![]() |
|
Camp town usa ![]() Newbie ![]() Joined: 26 Sep 2020 Location: Wi Online Status: Offline Posts: 32 |
![]() |
ordered, thanks!
|
|
![]() |
|
pedwards2932 ![]() Senior Member ![]() Joined: 21 Sep 2020 Online Status: Offline Posts: 333 |
![]() |
![]() |
|
offgrid ![]() Senior Member ![]() Joined: 23 Jul 2018 Online Status: Offline Posts: 5290 |
![]() |
Yes NEC Article 551 discusses ac circuits. But that does not mean the NEC does not cover dc circuits. That is simply incorrect. Article 690 covers solar which is dc and article 480 covers battery installations, which are obviously also dc. In fact essentially all of the NEC is applicable to dc as well as ac systems. All the sections covering grounding, fuse and circuit breaker selection, conductor ampacity are equally applicable and need to be followed say for an off grid home to pass an electrical inspection. The reason it is better to first manually connect and disconnect the bolted battery negative terminal for maintenance purposes is because you can’t inadvertently short your tools to ground if you disconnect that first, then the positive. That maintenance activity has nothing to do with where you install a permanent switch like a battery disconnect. The article you are referring to claims that placing the disconnect in either positive or negative works “equally well”. I disagree. Every other switch, fuse, and circuit breaker in the trailer is in the positive leg, because FR is following the Code and good practice. That way you know that the grounded conductor (negative) is solid and any open circuit is in the positive leg. Why should the disconnect switch be any different? No explanation other than there might be a fuse block in the positive line which could make disconnect switch placement there inconvenient is given a a reason for placing the disconnect in the negative line. That is certainly not the case in an rpod, and even if it was inconvenience is not an excuse for violating code. I’d love to be a fly on the wall if an electrician tried that in on his local inspector. 😜 As for installing the switch, you can also just cut the existing positive conductor and install an inline switch if you have enough slack and you want to do it that way. Pedward’s suggestion to use a circuit breaker is a good one, that also will protect the conductor from the battery to the panel. Any 12V taters 40A breaker should work but do gets manual resettable one so you’re not waiting around for an automatic one to decide to reset. |
|
1994 Chinook Concourse
1995 RV6A Experimental Aircraft 2015 Rpod 179 - sold |
|
![]() |
|
Camp town usa ![]() Newbie ![]() Joined: 26 Sep 2020 Location: Wi Online Status: Offline Posts: 32 |
![]() |
There's a lot of options, of which I'm not sure which is appropriate. Does it matter automatic or manual reset? Can you simply point me to the applicable breaker I should order?
![]() |
|
![]() |
|
pedwards2932 ![]() Senior Member ![]() Joined: 21 Sep 2020 Online Status: Offline Posts: 333 |
![]() |
I used to work on boats which are essentially RVs on water.....never saw 12 volt shut off use the ground always used the positive. I suspect the worry is it would be easier to accidentally ground the system...not sure. The circuit breaker I used is a 40 amp and the one I got easily fit in the battery box and is easily resettable. I used the circuit breaker because there is no protection between the + side of battery to switch.
|
|
![]() |
|
Camp town usa ![]() Newbie ![]() Joined: 26 Sep 2020 Location: Wi Online Status: Offline Posts: 32 |
![]() |
Thanks again Pedwards, but one last question (maybe). In buying the disconnect switch i didn't also get a breaker to insert in between. What size breaker do i need? Is there any preference otherwise on type?
|
|
![]() |